Finally got the exact figures and setups for using two small Honda gensets instead of one large genset:
1 - You don't need the expensive, $275 30 amp, dual hook-up kit unless you are specifically needing the 30 amp receptacle. You can order the RV type 30 amp or the the twist lock 30 amp if you do need that.
2 - A single Honda 2000 outputs 13.3 amps continuous, 16.7 peak (30 min.)
3 - Two Honda 1000 units output 15 amps continuous, 16.7 peak.
4 - Connected with just the $29.95 wire set, you can take that 15 amp continuous, 16.7 amp peak, out of one, single plug-in, or you can distribute that load across any or all 4 plug-ins on the unit fronts.
5 - Two Honda 2000 units connected by the $29.95 wire set gives you:
One 20amp peak, 16 amp rated receptacle (note the 2000's receptacles take a 15 or 20 amp plug) and the second unit gives you 13.3 peak, 10.6 continuous split between the two receptacles on the front.
or...... you can split up to 33.3 amps peak and 26.7 amps continuous evenly drawn from both units' front four receptacles.
6 - Two Honda 2000 units give 4000 max, 3200 cont. Watts vs. 3000 max,
2800 cont. for the Honda 3000 unit.
7 - Two Honda 3000 units give Max of 6000 Watts, 50 amps and Continuous 5600 Watts, 46.7 Amps. Note that TWO Honda 2000s significantly out perform the 3000, and that THREE 2000 units would output more total than TWO 3000 units, although only two of the three would acutally be connected.
8 - Dramatic reductions in total weight per Watt/Amp as well as better Max and Continuous output, in all size levels, if one uses two smaller units instead of the larger.
John
1 - You don't need the expensive, $275 30 amp, dual hook-up kit unless you are specifically needing the 30 amp receptacle. You can order the RV type 30 amp or the the twist lock 30 amp if you do need that.
2 - A single Honda 2000 outputs 13.3 amps continuous, 16.7 peak (30 min.)
3 - Two Honda 1000 units output 15 amps continuous, 16.7 peak.
4 - Connected with just the $29.95 wire set, you can take that 15 amp continuous, 16.7 amp peak, out of one, single plug-in, or you can distribute that load across any or all 4 plug-ins on the unit fronts.
5 - Two Honda 2000 units connected by the $29.95 wire set gives you:
One 20amp peak, 16 amp rated receptacle (note the 2000's receptacles take a 15 or 20 amp plug) and the second unit gives you 13.3 peak, 10.6 continuous split between the two receptacles on the front.
or...... you can split up to 33.3 amps peak and 26.7 amps continuous evenly drawn from both units' front four receptacles.
6 - Two Honda 2000 units give 4000 max, 3200 cont. Watts vs. 3000 max,
2800 cont. for the Honda 3000 unit.
7 - Two Honda 3000 units give Max of 6000 Watts, 50 amps and Continuous 5600 Watts, 46.7 Amps. Note that TWO Honda 2000s significantly out perform the 3000, and that THREE 2000 units would output more total than TWO 3000 units, although only two of the three would acutally be connected.
8 - Dramatic reductions in total weight per Watt/Amp as well as better Max and Continuous output, in all size levels, if one uses two smaller units instead of the larger.
John